2 story building, 2nd floor corridor with total of 40 cumulative occupants that egress into the space. At each end of the corridor is an Exit Access. Is Exception 4 applicable?
2015 IBC SECTION 1020 CORRIDORS
1020.1 Construction
Corridors shall be fire-resistance rated in accordance with Table 1020.1. The corridor walls required to be fire-resistance rated shall comply with Section 708 for fire partitions.
Exception 4: A fire-resistance rating is not required for corridors in an occupancy in Group B that is a space requiring only a single means of egress complying with Section 1006.2.