An average day

49439774346_0701fec18b_b.jpg

There is water in the trench and much of the pipe is wet. The 180° change of direction will be eliminated along with the leak.

49439302633_09b51155fe_b.jpg
 
Last edited:
Are they placing the slab on the top soil?

It's so weird to see construction there. So different from here with our 4' frost depth.
 
The job is a re-roof. I was there or the final inspection. So I have to verify the smoke and CO alarms.

49452474816_536d0aff35_b.jpg

The dwelling is occupied but nobody was there. I called the phone number on the note to tell him that I do not enter occupied buildings without an escort. No answer....turns out to be the contractor's voice mail.
 
Last edited:
On a service upgrade do you always require GFCI protection for the pool pump motor?

49452533701_58cac12f70_b.jpg
 
Last edited:
I didn’t inspect that installation. I’ve seen more than a few carports that have an array for a roof. Would firemen get on the roof of a burning carport?
 
Pool pump motors require GFCI protection. ... According to 680.22(B), so yes i would hope my inspectors would catch that.

In as much as I have to write that correction every time there is a pool with a service upgrade....I'm certain that few inspectors require the GFCI.

I am not exaggerating about the "every time".
 
The job is a service upgrade. This is the water main. The contractor is an engineering firm that has a C-10 license. For everybody not in California, a C-10 is an electrical contractor and please stay where you are. Thanks for that.

49456637448_fb245d0252_b.jpg

Notice the clamp that secures the jumper to the wall. The work is completely wrong and completely right.


49457238281_fd069bfb53_b.jpg

Why do they think that the armor can be in the dirt?

49457238401_1b9ba37ebf_b.jpg

These pictures were taken on the same day....so I had at least three service upgrades on that day. I am just one of more than 1000 California inspectors. Hundreds are done every day and dozens are done by professional electricians.
 
Last edited:
The plumbing company is tied in with a couple of retailers so they do plenty of water heaters. They almost always up-sell with the expansion tank. It's a real money maker.

49483551171_ef57db7028_b.jpg

The installation instructions: (http://backstop.net/pdfdocs/BackStop Instructions.pdf) state that the tank should be 18" away from the heater with the tank vertical and the pipe that it's attached to, supported. There is a an air valve on the bottom for checking the charge. Or as in this case, not.

49483551541_dc9095cfd7_b.jpg

This is a rarity.
This is confusing in that the reason it is rare has to do with the placement of the valve which is usually attached to the end of the hard pipe with the connector screwed to it. The sediment trap is installed correctly and that is not so rare. I'd say about 50/50 on the trap.

49483066038_a7a5e602d6_c.jpg
 
Last edited:
This is typical:

49486007292_38de561e3d_b.jpg

Look at the vertical segment of pipe. It seems to me that it should be secured from acting as a lever and either tightening or loosening the upstream pipe fittings. And that's what I told them. What is bothersome is that I had to tell them at all. This type of error tells me that the worker had no training on gas pipe. None. This mistake has got to be on the first page.
 
Last edited:
Post #3912
Pic #1, No anti-siphon device on the sillcock requirement in CA? Is it possible that the valve was installed prior to code requirement?

Pic #2, Ground rod sticking up grade, preferred it be below grade at inspection but visible. If the armor wasn't touching the earth would you consider that a daisy chain grounding system and allow?

Pic #3, I think the code allows the ground wire below the sidings edge without conduit protection. Here in the mid-west, a house service waterline can't be exposed like that because of freezing.

Post 3913
Pic #2, Flue pipe needs 6-inch clearance from combustibles and flue fasteners?

Post 3915, That sediment trap makes no sense in that location, would it make sense to replace the lower elbow with a tee and install the leg at that location? You got your pipe dope for sure!
 
Post #3912
Pic #1, No anti-siphon device on the sillcock requirement in CA? Is it possible that the valve was installed prior to code requirement?
Answer 1. Ca does require an anti siphon device. I have never written the correction.

Pic #2, Ground rod sticking up grade, preferred it be below grade at inspection but visible. If the armor wasn't touching the earth would you consider that a daisy chain grounding system and allow?
Answer 2. 10' rod....or so they say. 6" from 8' is not worth the grief. I don't know what you mean by daisy chain.

Pic #3, I think the code allows the ground wire below the sidings edge without conduit protection. Here in the mid-west, a house service waterline can't be exposed like that because of freezing.
Answer 3. That is true enough but when the conductor spans between the house and the rod it is exposed to physical damage. Beyond that, it is a west coast thing to always have cable armor protecting the GEC.


Post 3913
Pic #2, Flue pipe needs 6-inch clearance from combustibles and flue fasteners?
Answer post 3913. Yes.

Post 3915, That sediment trap makes no sense in that location, would it make sense to replace the lower elbow with a tee and install the leg at that location? You got your pipe dope for sure!
Answer post 3915. So now you expect things to make sense? Do you have a code section for that?
 