I appreciate all of the interesting photos you post of the often "shoddy" work you find. I'm curious though for this one, what exactly is the violation here? Definitely could be one, but I don't see it immediately. Are you complaining about the crimped connection? Looks not-removable to me. and it looks like the actual grounding electrode conductor is one continuous piece, looks big enough, and the armor clad is not even required if that's #6 or larger.
 
I appreciate all of the interesting photos you post of the often "shoddy" work you find. I'm curious though for this one, what exactly is the violation here? Definitely could be one, but I don't see it immediately. Are you complaining about the crimped connection? Looks not-removable to me. and it looks like the actual grounding electrode conductor is one continuous piece, looks big enough, and the armor clad is not even required if that's #6 or larger.
The wire is #4. The armor shall be bonded at every end. The wire is subject to physical damage and requires protection no matter what size it is.
 
The wire is #4. The armor shall be bonded at every end. The wire is subject to physical damage and requires protection no matter what size it is.
Is that a drive way? Or are you using 250.64 (B)(2) to say that's exposed to physical damage? (2019 CEC) If that's a driveway I'd agree, if it's just a walkway I'd say 250.64 (B)(1) "A 6 AWG or larger copper or aluminum grounding electrode conductor not exposed to physical damage shall be permitted to run along the surface of the building construction without metal covering or protection" would allow this install w/o the protection and therefore if extra protection is added the way it's shown it's not a violation. This comes down to interpretation and opinion, a very grey and sticky area of the code.
 
I am seeing this more often. I think that they see a button and assume it is GFCI. Others probably don't know the difference. Sme see the word "combination" and assume the breaker has both. I also think that far too many inspectors miss this.

14.pngI



20210121_112123.jpeg

20210121_111412.jpeg


20210121_111420.jpeg
 
Is that a drive way? Or are you using 250.64 (B)(2) to say that's exposed to physical damage? (2019 CEC) If that's a driveway I'd agree, if it's just a walkway I'd say 250.64 (B)(1) "A 6 AWG or larger copper or aluminum grounding electrode conductor not exposed to physical damage shall be permitted to run along the surface of the building construction without metal covering or protection" would allow this install w/o the protection and therefore if extra protection is added the way it's shown it's not a violation. This comes down to interpretation and opinion, a very grey and sticky area of the code.
Is this me setting a bad example for the rest of us again?
 
I would agree that it is "mostly" along the building construction, so yes, judgment call.....But bonding both ends of the metal "raceway" is not gray at all....250.64E1
 
Is this me setting a bad example for the rest of us again?
Well yes and no. You are correct with regards to the question of whether protection is required. It is apparent that the contractor is in the "it needs protection camp".

I disagree with the contention that "extra" stuff can be provided incorrectly since it is not required to be there. The reason behind the bonding of every end of ferrous metal raceway that protects a GEC has to do with capacitive coupling. How to spell it is where my understanding hesitates. Electric fields inducing a current is for the engineers to explain but suffice it to say the work in the picture is a violation.

A further violation shown is the C-tap. While the C-tap is legal to use, it is not properly crimped as there are no witness marks of a proprietary crimping tool having been utilized.

20210111_094825.jpeg
 
Well yes and no. You are correct with regards to the question of whether protection is required. It is apparent that the contractor is in the "it needs protection camp".

I disagree with the contention that "extra" stuff can be provided incorrectly since it is not required to be there. The reason behind the bonding of every end of ferrous metal raceway that protects a GEC has to do with capacitive coupling. How to spell it is where my understanding hesitates. Electric fields inducing a current is for the engineers to explain but suffice it to say the work in the picture is a violation.

A further violation shown is the C-tap. While the C-tap is legal to use, it is not properly crimped as there are no witness marks of a proprietary crimping tool having been utilized.

View attachment 7420
Cool, some new stuff to look up! Love it. So if the contractor had simply omitted the AC it would have been ok, but since it's there it needs to be installed correctly. I can get with that logic. I'll do my research, but do you know if the capacitive coupling would occur during normal operation, or only when there's a fault? Or a lightning strike? Thanks for explaining.
 
I would agree that it is "mostly" along the building construction, so yes, judgment call.....But bonding both ends of the metal "raceway" is not gray at all....250.64E1
Would you consider the AC a raceway or an enclosure? In my mind a raceway or an enclosure brings up very specific things, AC is not one of them, but I'm open to understanding things differently.
 
as there are no witness marks of a proprietary crimping tool having been utilized.
Do you have a clear picture of a properly crimped dealie?
 
Cool, some new stuff to look up! Love it. So if the contractor had simply omitted the AC it would have been ok, but since it's there it needs to be installed correctly. I can get with that logic. I'll do my research, but do you know if the capacitive coupling would occur during normal operation, or only when there's a fault? Or a lightning strike? Thanks for explaining.
During normal operation the GEC and electrodes see no current. Only if there is a blast from lightning, or commingling higher voltage lines with medium voltage would there be a significant role to play. At least that has been explained that way.....but hey now this is the internet and all.
 
Last edited:
as there are no witness marks of a proprietary crimping tool having been utilized.
Do you have a clear picture of a properly crimped dealie?
I have over 100 pictures of wrong C-taps and no pictures of proper C-taps. The Tool is supposed to emboss a number in the witness mark. That number is supposed to match the die used that is the right die for the size C-tap. When it is there it is so faint that it is nearly undetectable. Not all manufacturers have that specific tool either. The thing to look for is a straight sided rectangular indent and a damn tight crimp.

The first picture comes close. It looks like a crimper that was fit for the task was used. There appears to be two crimps as would be expected. The trouble is that there are four wires when only two are allowed. Well in all fairness, it's soon to be three wires.

IMG_5310.jpeg


An angry electrician was loose on this one.


IMG_3817.jpeg


Pliers were used.


IMG_3400.jpeg


The last one looks like it had a little bit of both.

IMG_3508.jpeg
 
Last edited:
A problem with virtual inspections pops up when I see something in a picture that raises questions and I have to wait for an answer. I saw this fitting and now I gotts tah know.

IMG_7002.jpeg


IMG_7001.jpeg
 
That Myers type hub certainly is not being used according to it's listing, and I'd almost be willing to bet that hub cost Larry, Curly, & Moe's Electric more money then the proper interchangeable hub.
 
Another inspector has this job. The panel was mounted over a hole in the exterior stucco wall which is not permitted. The missing kos have been plugged. We have a few ways to get the conductors into the new panel....this is not one of them.