Maybe the bolt doesn't project far enough above the plate for the threads to catch once a washer is installed?
I am not sure about there being enough bolt above the plate...I am sure that there is a whole lot of hole for the bolt. The hole is permitted to be 1/16" larger than the bolt.
 
I am not sure about there being enough bolt above the plate...I am sure that there is a whole lot of hole for the bolt. The hole is permitted to be 1/16" larger than the bolt.
California rule? Seismic?
 
Contractor did an entire dwelling re-pipe with stainless steel pipe and fittings. I have never seen such a thing.

IMG_1535 2.JPG

IMG_1535.JPG

IMG_1537.JPG
IMG_1536.JPG
 
P2903.3.1 Maximum pressure.
The static water pressure shall be not greater than 80 psi (551 kPa). Where the main pressure exceeds 80 psi (551 kPa), an approved pressure-reducing valve conforming to ASSE 1003 or CSA B356 shall be installed on the domestic water branch main or riser at the connection to the water service pipe.

We have some areas in the city that the operating pressure is 90 to 95 PSI
 
P2903.3.1 Maximum pressure.
The static water pressure shall be not greater than 80 psi (551 kPa). Where the main pressure exceeds 80 psi (551 kPa), an approved pressure-reducing valve conforming to ASSE 1003 or CSA B356 shall be installed on the domestic water branch main or riser at the connection to the water service pipe.

We have some areas in the city that the operating pressure is 90 to 95 PSI
The picture has a TPR-valve one would find on a water heater, not a conventional pressure reducing valve. It even has the BTU limits on it.

1614282679207.png
 
You would think that if he can afford all of that stainless steel piping he could afford the proper pressure reducer...
 
I am not sure what this is all about. I do know that an extensive addition was built with an indoor swimming pool on the second floor. There is a 400 amp service and several sub-panels. I was asked to inspect a solar project when they sent this picture. I found that the permits for the addition are still listed as open when I look at the computer records....so naturally I declined to inspect the solar until the roof that it's on has has passed a final inspection. The contractor is adamant that the previous inspector approved everything related to the addition. That inspector concurred so I declined to inspect the solar because that inspector concurred.


17-cold water bond.jpg
 
Last edited:
I wish you would learn to speak english. I understand why you declined to pass the array with the roof permit open, but why did you refuse when you learned the other inspector passed the roof? Are you just waiting for him to close that permit?
 
Are you just waiting for him to close that permit?
Ya...Ya, that’s the ticket.

I didn’t decline to pass the array, I declined to inspect the array. The picture shows some electrical hardware that’s been cobbled together and an inspector approved it. There’s a 400amp service panel, one 200amp panel and two 100amp panels. There’s a second floor indoor pool. There’s an elevator. There’s several furnaces.

I met the contractor early in the project. I know the inspector that approved the final inspection...including the ground clamp.

I don’t want my name on any part of it.
 