This is an AC disconnect for a solar installation. It is the make and model that's specified on the plans. It is mounted on the back wall of the house near the service panel. There is no dead-front protection. That doesn't sound safe at all. I will challenge this.
Instead of utilizing the hole that the panel manufacturer provided for mounting a grounding lug, the installer drilled a hole and put the lug there. There are no WEEB clips under the lugs. The ground path is relying on a star lock washer.
This is all over the installation.
The bus is rated 200 amps....the mains are 200 amps....split bus panelboard will not allow a 20% increase....there is no room for the 40 amp solar contribution.

Instead of utilizing the hole that the panel manufacturer provided for mounting a grounding lug, the installer drilled a hole and put the lug there. There are no WEEB clips under the lugs. The ground path is relying on a star lock washer.

This is all over the installation.

The bus is rated 200 amps....the mains are 200 amps....split bus panelboard will not allow a 20% increase....there is no room for the 40 amp solar contribution.