I am trying to interpret a few things mainly including "Building" and "exit discharge". Quick code items = type II-B, full concrete construction, fully sprinklered, Business occupancy, 462 total occupants, 24,217 total SF (1st & 2nd floors), V-22 flood zone.
We have an elevated building in a Velocity Zone so we have our building elevated up out of the flood plane. I am reading the building definition [Any structure used or intended for supporting or sheltering any use or occupancy] as a structure [That which is built or constructed] is not the under building space because it is not allowed to be occupied and technically has no occupancy. Then we get to the egress stairs, we have 3, two of which are in shafts that go from ground level to 2nd floor. If you read Exit Discharge [That portion of a means of egress system between the termination of an exit and a public way.] the stair is the exit access, the doors on the ground level are the exit, and the open air space under the building (27' for Stair A and 35' for Stair B) is the exit discharge. Even OSHA has that their exit discharge is, 1910.36(c)(1) Each exit discharge must lead directly outside or to a street, walkway, refuge area, public way, or open space with access to the outside.
There was a comment early on that development services thought that it is under the roof / floor and thus part of the building. I believe that the code reads that the ground level is part of the area, but not part of the building. The suggestion of using exit passageways [An exit component that is separated from other interior spaces of a building or structure by fire-resistance-rated construction and opening protectives and provides for a protected path of egress travel in a horizontal direction to an exit or to the exit discharge. ] doesn't make sense due to not having any "interior" areas other than the elevator and stair shafts. We would then need to A/C and ventilate this space, but can't because of the Design Flood Elevation.
I am curious on others interpretations and if other that design in flood zones what their take is.... We do not think that we need to create an enclosed passageway to the underside of the exterior wall. The underside of the building is all open air.
Thoughts / comments?
I am trying to interpret a few things mainly including "Building" and "exit discharge". Quick code items = type II-B, full concrete construction, fully sprinklered, Business occupancy, 462 total occupants, 24,217 total SF (1st & 2nd floors), V-22 flood zone.
We have an elevated building in a Velocity Zone so we have our building elevated up out of the flood plane. I am reading the building definition [Any structure used or intended for supporting or sheltering any use or occupancy] as a structure [That which is built or constructed] is not the under building space because it is not allowed to be occupied and technically has no occupancy. Then we get to the egress stairs, we have 3, two of which are in shafts that go from ground level to 2nd floor. If you read Exit Discharge [That portion of a means of egress system between the termination of an exit and a public way.] the stair is the exit access, the doors on the ground level are the exit, and the open air space under the building (27' for Stair A and 35' for Stair B) is the exit discharge. Even OSHA has that their exit discharge is, 1910.36(c)(1) Each exit discharge must lead directly outside or to a street, walkway, refuge area, public way, or open space with access to the outside.
There was a comment early on that development services thought that it is under the roof / floor and thus part of the building. I believe that the code reads that the ground level is part of the area, but not part of the building. The suggestion of using exit passageways [An exit component that is separated from other interior spaces of a building or structure by fire-resistance-rated construction and opening protectives and provides for a protected path of egress travel in a horizontal direction to an exit or to the exit discharge. ] doesn't make sense due to not having any "interior" areas other than the elevator and stair shafts. We would then need to A/C and ventilate this space, but can't because of the Design Flood Elevation.
I am curious on others interpretations and if other that design in flood zones what their take is.... We do not think that we need to create an enclosed passageway to the underside of the exterior wall. The underside of the building is all open air.
Thoughts / comments?