Exit Path width
  • Thread starter Thread starter TZJR
  • Start date Start date
T
TZJR
Guest
Good morning everyone,
I need to confirm a question on an exit path set of egress doors, We need to shift the mid landing of a switch back ramp to the left because of a clearance issue at the top of the ramp. below you will see a pair of 36" doors exiting the building, from the back side of the ramp to the doors used to be 96" and i am reducing it to 74.25" to clear a path on the upper side. This is still larger than the 72" wide doors, does anyone see any issue i am missing (PA 2015 building code), ANSI A117.1 or 2010-ADA.
Steveray,
Just for my confirmation with you, you are referring to 1005.3.2 "Egress capacity factor per person", correct?
The reason I ask, the stairways section, in 1005.3.1 notes 0.3, which does not exit here but the ramp base for convergence is there, 1005.3.2 notes for everything else except stairs 0.2
1005.3.2 Other egress components. The capacity, in
inches, of means of egress components other than stairways
shall be calculated by multiplying the occupant load
served by such component by a means of egress capacity
factor of 0.2 inch (5.1 mm) per occupant.
If this building is equipped with automatic fire sprinkler system and emergency voice/alarm communication system and occupancy is other than H or I-2, than egress capacity factor can be further reduced to 0.15 inch per occupant. See 1005.3.2 exception 1.
Thanks Steveray, that is what I wanted to confirm.