Exterior Door Fire Rating

Charles NYC

REGISTERED
Joined
May 4, 2020
Messages
3
Location
NYC
Working on a Type IA construction residential project with a sprinkler system. If the entrance door is at the property line does it need to have a fire rating?
 
Welcome to the forum. If you find your answer, think of contributing by becoming a paid member.

You cannot have an opening within 3-ft regardless of construction type.


**NY IBC**
upload_2020-5-4_15-36-10.png
 
Last edited:
You cannot have an opening within 3-ft regardless of construction type.

View attachment 6634
Wait.... is this per the IRC or IBC?

I see now that you note residential, but you also called out Type IA construction.

Although, it will not matter much, as per IRC Table 302.1(1) openings within 3-ft are not permitted either.
 
Working on a Type IA construction residential project with a sprinkler system. If the entrance door is at the property line does it need to have a fire rating?


If I keep walking straight,,,,, where does that take me??

Middle of the street??

Or how far till I hit another building?
 
Can you explain that. If the exterior building wall is on the prop line ... no doors allowed?
 
Ok... a bit more of the picture now. If it is facing a public way or street, read through the following code section. If it is 3-ft to a property line where the adjoining parcel may be built upon, see the Table (cropped to only include 0-3 and 3-5).