Our town recently built a new fire station with 12 sleeping rooms. We required Emergency Escape and Rescue Openings and interconnected smoke detectors for each sleeping room plus CO detectors in the adjoining hallways. The building was also fully protected by an automatic sprinkler system.
Our town recently built a new fire station with 12 sleeping rooms. We required Emergency Escape and Rescue Openings and interconnected smoke detectors for each sleeping room plus CO detectors in the adjoining hallways. The building was also fully protected by an automatic sprinkler system.
Do you have more than 10 firefighters on duty during one shift? If not it would be an R-3 and EERO will be required
310.3 Residential Group R-1.
Residential occupancies containing sleeping units where the occupants are primarily transient in nature, including:
Boarding houses (transient) with more than 10 occupants
Congregate living facilities (transient) with more than 10 occupants
CONGREGATE LIVING FACILITIES. A building or part thereof that contains sleeping units where residents share bathroom and/or kitchen facilities.
TRANSIENT. Occupancy of a dwelling unit or sleeping unit for not more than 30 days.
310.5 Residential Group R-3.
Residential occupancies where the occupants are primarily permanent in nature and not classified as Group R-1, R-2, R-4 or I, including:
Buildings that do not contain more than two dwelling units
Boarding houses (nontransient) with 16 or fewer occupants
Boarding houses (transient) with 10 or fewer occupants
Care facilities that provide accommodations for five or fewer persons receiving care
Congregate living facilities (nontransient) with 16 or fewer occupants
Congregate living facilities (transient) with 10 or fewer occupants
The plans were submitted in early 2016, approved in 2017, and were designed using the 2014 Oregon Structural Specialty Code (which was based upon the 2012 IBC). The building was completed in early 2019.2015 Edition or other?
Transient or Non-Transient it really does not matter except for applying the code requirements which need to be the same no matter if they are fire fighters or a resident in a hospital or any other 24 hour shift job that you maybe able to sleep during a down time
The code does not address everything and sometimes we just have to make a decision right or wrong and stick with it.
ICC's 2015 re-write of EERO's really complicated things from the previous Editions. Pay special ATTENTION to Tables 1006.3.2(1) and 1006.3.2(2) as referenced. Generally speaking, a sprinklered building with two exits off the Story DOES NOT require EERO's. The occupants (fire fighters) in the R Occupancy are considered non-transient (i.e. they are familiar with their surroundings, un-like a Hotel occupancy). If the "calculated" occupant load of the residential area is less than 16, the occupancy can be classified as an R3, if greater than 16 then the Occupancy is R2. Note, the R3 Occupancy has no handicap requirements (bad idea) and the R2 Occupancy must be Type B Accessible Sleeping and bathing units (better but still not great). What I have typically done is to provide fully accessible (ANSI A117) bathing facilities in the "public" accessible restroom and make the sleeping quarters Type B Accessible. Other Occupancies that are typical in a Fire Station are S2, B and A3 (meeting rooms).
Ken
CDA: I think you could argue an R1 Occupancy (pointing out the R1 requirements are more restrictive than an R2), however one of your First Story Units (including bathing facilities) would have to be fully Accessible (ANSI A117). This might be a pretty big trade-off to not have EERO.Agree, trying to get to where I can say EERO not required. That is why I thought R-1
Only showing one stair off second floor, about ten occupant load.
And two bedrooms on the first floor.
my firm does a lot of fire stations, and we typically classify them as non-separated mixed use B, S-2 & R-2 and have never had it questions by the local AHJ.
B = administrative areas
S-2 = apparatus bays & equipment storage
R-2 = sleeping quarters
Sometimes we also have to add an A occupancy into the mix depending on how large the assembly spaces get (day room, gym, training rooms).
Agree with Tim R-2 for sleeping occupancy in a mixed use building. I see nothing in the code that requires a EERO in a R2. For the comfort of the room occupant a window that operates is nice.