That does not address hip rafter sizing. It may impose a requirement for additional details to provide the "continuous ties across the structure" referenced.R802.2
Cheers, Wayne
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
That does not address hip rafter sizing. It may impose a requirement for additional details to provide the "continuous ties across the structure" referenced.R802.2
Wrong.For a simple hip of length L, if it needed to be designed as a beam, the tributary area is 1/2*L^2.
Agree. This is why I am bringing this up again.Wrong.
The tributary area is not uniform on a hip or valley. Running calculations, as is necessary, requires that the distributed load be reflective of the tributary area acting on the member. The load may start at 70lbs (i.e. 2' jacks each side; length / 2 * 2 sides = 2'/2*2*35psf=70lbs), but at the end could be 280lbs (i.e. 8' jacks each side; 8'/2*2*35=280lbs). The load is not equally distributed across the member. This can also put one end of the member at risk for shear failure.
Ah, yes, working with horizontally projected distances and lengths, 1/2 * L^2 is the tributary area not when L is the hip length, but when L is the common rafter length. If M is the hip length, M = sqrt(2) * L, and so the tributary area would be 1/4 * M^2.Wrong.
Agreed, and I take no issue with your subsequent comments, but as the topic of the thread is IRC prescriptive design for a hip rafter, per R802.4.4 such design considerations are only required when the roof slope is below 3:12.The tributary area is not uniform on a hip or valley.
You are forgetting about the second sentence that discusses the assembly.That does not address hip rafter sizing
This is prescriptive for connection support but has nothing to do with loading as previously stated. The section is misleading if you read it the way you do.Ah, yes, working with horizontally projected distances and lengths, 1/2 * L^2 is the tributary area not when L is the hip length, but when L is the common rafter length. If M is the hip length, M = sqrt(2) * L, and so the tributary area would be 1/4 * M^2.
Agreed, and I take no issue with your subsequent comments, but as the topic of the thread is IRC prescriptive design for a hip rafter, per R802.4.4 such design considerations are only required when the roof slope is below 3:12.
Cheers, Wayne
I believe you are referring to "The assembly shall be designed and constructed in accordance with the provisions of this chapter and Figures R606.11(1), R606.11(2) and R606.11(3) or in accordance with AWC NDS." So it suffices to comply with the rest of R802, i.e. R802.2 imposes no sizing requirements on its own.You are forgetting about the second sentence that discusses the assembly.
The rafter span tables are for uniformly loaded rafters.Ah, yes, working with horizontally projected distances and lengths, 1/2 * L^2 is the tributary area not when L is the hip length, but when L is the common rafter length. If M is the hip length, M = sqrt(2) * L, and so the tributary area would be 1/4 * M^2.
Agreed, and I take no issue with your subsequent comments, but as the topic of the thread is IRC prescriptive design for a hip rafter, per R802.4.4 such design considerations are only required when the roof slope is below 3:12.
Cheers, Wayne
Agreed that the rafter span tables do not apply to hips. Moreover, the rafter span tables refer to rafter spacing, and the hip is a singular member, not a repetitive one.The rafter span tables are for uniformly loaded rafters.
Are you referring to R802.4.4? It precisely covers the hip rafter, and when you have to design it as a beam for its loading. It's not about connection details.This is prescriptive for connection support but has nothing to do with loading as previously stated. The section is misleading if you read it the way you do.
Oh, if I were to build a hip roof from scratch, I'd go with the WFCM or an engineered design. As it certainly sounds like the prescriptive allowances in IRC R802 are too lax.That said, if you feel confident with the methodology you describe, I hope the best. I see an inevitable failure of any roof designed in such a way.
Some interesting discussion here on the complexities involved: https://www.eng-tips.com/viewthread.cfm?qid=392097Caveat: I have not look at an engineering analysis of how the forces resolve in a hip roof--it is fairly complicated.
Do tell.Luckily the energy code doesn't really allow stick framed roofs anymore in our climate zone.....
or 10 inches of closed cell spray foamR60= 20" of fiberglass
There is more than one material & method for insulation compliance, but I get it. When you are use to doing things one way and one way only, change is hard.R60= 20" of fiberglass...So even if you built with 2x12 rafters and ceiling joist in a raised heel rafter configuration, you are hard pressed to get 20" with proper ventilation in place..
Which is still basically 2x12 framing minimum even on a small roof...or 10 inches of closed cell spray foam
Maybe that’s cheaper than paying for engineer trussesWhich is still basically 2x12 framing minimum even on a small roof...
R60= 20" of fiberglass...So even if you built with 2x12 rafters and ceiling joist in a raised heel rafter configuration, you are hard pressed to get 20" with proper ventilation in place...
View attachment 11074
And then of course you need to figure out how to deal with roof thrust....
You quoted the section on Ceilings Without Attics. The preceding section "N1102.2.1 (R402.2.1) Ceilings With Attics" does not have that 500sf/20% limit.The noted section does not entirely resolve the issue, particularly given the sentence I put in green text, but the 500sf/20% would definitely help
I don't agree Wayne.You quoted the section on Ceilings Without Attics. The preceding section "N1102.2.1 (R402.2.1) Ceilings With Attics" does not have that 500sf/20% limit.
As I read it, you basically put R-60 over the entire ceiling where it fits, and where it gets squished at the eaves, that's fine.
Cheers, Wayne