You would find that in the listed and tested fire penetration detail from the firestop material manufacturer...
How many floors can a non-rated shaft penetrate?4"
I have more info: It's a 4" future radon pipe penetrating 4 floors, not a wall. R-2, Type 5 construction.
Not a shaft.How many floors can a non-rated shaft penetrate?
713.1 General. The provisions of this section shall apply to shafts required to protect openings and penetrations through floor/ceiling and roof/ceiling assemblies. Interior exit stair- ways and ramps shall be enclosed in accordance with Section 1023.
714.5 Nonfire-resistance-rated assemblies. Penetrations of nonfire-resistance-rated floor or floor/ceiling assemblies or the ceiling membrane of a nonfire-resistance-rated roof/ceiling assembly shall meet the requirements of Section 713 or shall comply with Section 714.5.1 or 714.5.2.
714.5.1 Noncombustible penetrating items. Noncombustible penetrating items that connect not more than five stories are permitted, provided that the annular space is filled to resist the free passage of flame and the products of combustion with an approved noncombustible material or with a fill, void or cavity material that is tested and clas- sified for use in through-penetration firestop systems.
714.5.2 Penetrating items. Penetrating items that connect not more than two stories are permitted, provided that the annular space is filled with an approved material to resist the free passage of flame and the products of combustion.
Not a shaft.
If the pipe remains internal to the wall, then it will only require fireblocking at plate lines.
Oh, well I thought he said that four floors were being penetrated. I guess I added an in where it didn't belong.
"I have more info: It's a 4" future radon pipe penetrating 4 floors, not in a wall. R-2, Type 5 construction."
https://www.hilti.com/c/CLS_FIRESTOP_PROTECTION_7131/CLS_FIRESTOP_COLLAR_WRAP_BANDAGE_7131/r373?CHD_NOMINAL_PIPE_DIAMETER=4-11/32 in&combo_content=884a6325c5f164f3cc6d5f97bd3e3231&itemCode=304329
And your main question is,,,,
Does it require a sleeve???
Yes, sleeve.