From 2009
See exception 1
SECTION 1029 EMERGENCY ESCAPE AND RESCUE
1029.1 General. In addition to the means of egress required by this chapter, provisions shall be made for emergency escape and rescue in Group R and I-1 occupancies. Basements and sleeping rooms below the fourth story above grade plane shall have at least one exterior emergency escape and rescue opening in accordance with this section. Where basements contain one or more sleeping rooms, emergency escape and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Such openings shall open directly into a public way or to a yard or court that opens to a public way.
1. In other than Group R-3 occupancies, buildings equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. In other than Group R-3 occupancies, sleeping rooms provided with a door to a fire-resistance-rated corridor having access to two remote exits in opposite directions.
3. The emergency escape and rescue opening is permitted to open onto a balcony within an atrium in accordance with the requirements of Section 404, provided the balcony provides access to an exit and the dwelling unit or sleeping unit has a means of egress that is not open to the atrium.
4. Basements with a ceiling height of less than 80 inches (2032 mm) shall not be required to have emergency escape and rescue windows.
5. High-rise buildings in accordance with Section 403.
6. Emergency escape and rescue openings are not required from basements or sleeping rooms that have an exit door or exit access door that opens directly into a public way or to a yard, court or exterior exit balcony that opens to a public way.
7. Basements without habitable spaces and having no more than 200 square feet (18.6 m2) in floor area shall not be required to have emergency escape windows.
This section requires emergency escape and rescue provisions in groups where occupants may be sleeping during a potential fire buildup, but are capable of self-preservation (Groups R and I-1). A basement and each sleeping room are to be provided with an exterior window or door that meets the minimum size requirements and is operable for emergency escape by methods that are obvious and clearly understood by all users. Sleeping rooms four stories or more above grade are not required to be so equipped, since fire service access at that height, as well as escape through such an opening, may not be practical or reliable. In accordance with Chapter 9, such buildings will also be equipped throughout with an automatic fire suppression system. The provision for basements is in recognition that such types of spaces typically only have a single path of egress and often have no alternative routes available as other levels do.
It is important to note that this window is an element of escape and does not comprise any part of the means of egress unless it is a door with appropriate egress component characteristics.
Exception 1 assumes that the automatic sprinkler system can control fire buildup and reduce, if not eliminate, the need for an occupant to use an emergency escape window. The exception applies to buildings equipped throughout with an NFPA 13 or 13R sprinkler system.
Exception 2 allows another acceptable means of escape; that is, a door directly from the sleeping room to a corridor with exits in opposite directions, to substitute for the escape window.
Exception 3 provides for dwelling and sleeping units that have egress windows to a balcony that is within an atrium. The exception specifies that the dwelling or sleeping unit is to have another means of egress that does not pass through the atrium so that an independent route of egress is provided.
Exceptions 4 and 7 are intended to exempt basements that would not be likely to have sleeping rooms in them from the requirement to have emergency escape and rescue openings.
Exception 5 is in correlation with the exception for emergency escape windows in high-rise buildings addressed in Section 403.4.
The intent of Exception 6 is to permit sleeping rooms with a direct access to an exterior-type environment, such as a street or exit balcony, to not have an emergency escape window. The open atmosphere of the escape route would increase the likelihood that the means of egress be available even with the delayed response time for sleeping residents.