Okay well our code guy reached out to his local state group of building officials and got strong support for his interpretation on 1029 applicability. So we went back to the Fire Guy today--wish us luck.
this might be helpful for anyone working on this issue. We were forwarded this IBC item regarding 1029 applicability.
IBC Code Correlation Committee Code Proposal
BC27–09 CCC 1029.1 (IFC 1029.1)
Proponent: Sarah A. Rice, C.B.O., representing self
Revise as follows: 1029.1 (IFC 1029.1)
General. In addition to the means of egress required by this chapter, provisions shall be made for emergency escape and rescue in Group R and I-1 R-3 occupancies.
Basements and sleeping rooms below the fourth story above grade plane shall have at least one exterior emergency escape and rescue opening in accordance with this section.
Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement.
Such openings shall open directly into a public way or to a yard or court that opens to a public way.
Exceptions:
1. In other than Group R-3 occupancies, buildings equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. In other than Group R-3 occupancies, sleeping rooms provided with a door to a fire-resistance-rated corridor having access to two remote exits in opposite directions.
3. The emergency escape and rescue opening is permitted to open onto a balcony within an atrium in accordance with the requirements of Section 404, provided the balcony provides access to an exit and the dwelling unit or sleeping unit has a means of egress that is not open to the atrium.
4.1. Basements with a ceiling height of less than 80 inches (2032 mm) shall not be required to have emergency escape and rescue windows.
5. High-rise buildings in accordance with Section 403.
6.2. Emergency escape and rescue openings are not required from basements or sleeping rooms that have an exit door or exit access door that opens directly into a public way or to a yard, court or exterior exit balcony that opens to a public way.
7.3. Basements without habitable spaces and having no more than 200 square feet (18.6m2) in floor area shall not be required to have emergency escape windows.
Reason: The proposal is intended to revise and eliminate outdated material. Group I-1 and all R occupancies are required to protected by automatic sprinkler system per sections 903.2.5 and 903.2.7, respectively.
Existing exception #2 exempts all occupancies other than R-3 when protected by a sprinkler system.
Thus Section 1029 only applies to R-3 occupancies and the exceptions related to other occupancies can be deleted.
Specifically
Exception 1 is the sprinkler exception; it is not needed.
Exception 2 only applies to occupancies other than R-3; therefore it is not needed.
Exception 3 applies in atriums; atriums are unlikely to have R-3 occupancies.
Exception 5 applies to High-rise buildings which have to have a sprinkler system per section 403, thus they have been exempted twice.
These provisions are remnants from the time when the code did not require sprinkler protection in all R and I-1 occupancies and are no longer needed.
Arguments that these exceptions should not be eliminated because some jurisdictions do not require sprinklers for all R-occupancies, or that they use it for guidance of existing structures which are not sprinklered should not be a consideration.
If jurisdictions are amending the code to eliminate requirements, they should be balancing that with appropriate additions.
This section should not be used for existing buildings. Cost Impact: The code change proposal will not increase the cost of construction. ICCFILENAME:Rice-E3-1029.1
this might be helpful for anyone working on this issue. We were forwarded this IBC item regarding 1029 applicability.
IBC Code Correlation Committee Code Proposal
BC27–09 CCC 1029.1 (IFC 1029.1)
Proponent: Sarah A. Rice, C.B.O., representing self
Revise as follows: 1029.1 (IFC 1029.1)
General. In addition to the means of egress required by this chapter, provisions shall be made for emergency escape and rescue in Group R and I-1 R-3 occupancies.
Basements and sleeping rooms below the fourth story above grade plane shall have at least one exterior emergency escape and rescue opening in accordance with this section.
Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement.
Such openings shall open directly into a public way or to a yard or court that opens to a public way.
Exceptions:
1. In other than Group R-3 occupancies, buildings equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. In other than Group R-3 occupancies, sleeping rooms provided with a door to a fire-resistance-rated corridor having access to two remote exits in opposite directions.
3. The emergency escape and rescue opening is permitted to open onto a balcony within an atrium in accordance with the requirements of Section 404, provided the balcony provides access to an exit and the dwelling unit or sleeping unit has a means of egress that is not open to the atrium.
4.1. Basements with a ceiling height of less than 80 inches (2032 mm) shall not be required to have emergency escape and rescue windows.
5. High-rise buildings in accordance with Section 403.
6.2. Emergency escape and rescue openings are not required from basements or sleeping rooms that have an exit door or exit access door that opens directly into a public way or to a yard, court or exterior exit balcony that opens to a public way.
7.3. Basements without habitable spaces and having no more than 200 square feet (18.6m2) in floor area shall not be required to have emergency escape windows.
Reason: The proposal is intended to revise and eliminate outdated material. Group I-1 and all R occupancies are required to protected by automatic sprinkler system per sections 903.2.5 and 903.2.7, respectively.
Existing exception #2 exempts all occupancies other than R-3 when protected by a sprinkler system.
Thus Section 1029 only applies to R-3 occupancies and the exceptions related to other occupancies can be deleted.
Specifically
Exception 1 is the sprinkler exception; it is not needed.
Exception 2 only applies to occupancies other than R-3; therefore it is not needed.
Exception 3 applies in atriums; atriums are unlikely to have R-3 occupancies.
Exception 5 applies to High-rise buildings which have to have a sprinkler system per section 403, thus they have been exempted twice.
These provisions are remnants from the time when the code did not require sprinkler protection in all R and I-1 occupancies and are no longer needed.
Arguments that these exceptions should not be eliminated because some jurisdictions do not require sprinklers for all R-occupancies, or that they use it for guidance of existing structures which are not sprinklered should not be a consideration.
If jurisdictions are amending the code to eliminate requirements, they should be balancing that with appropriate additions.
This section should not be used for existing buildings. Cost Impact: The code change proposal will not increase the cost of construction. ICCFILENAME:Rice-E3-1029.1