Thanks Jim. I appreciate your patience, however, I still find it illogical (and yes I follow the line of code in what is referenced and not referenced) that the accessibility standards are applied to everything but the stairs, especially, in multi-level exemptions. As Mark said, there are other forms of disabilities to which the ANSI standards are designed to aide. I will sleep on it I guess, and hopefully when I wake up tomorrow morning eureka, I will have reconciled how a 3,000 SF, 2nd Floor, Non-Medical B Occupancy, is permitted to have a means of egress component that does not meet the specifications of the ANSI A117.1 (only a 48" width minimum and an area of refuge as required) because it is not considered an accessible route component and is not referenced in Chapter 10. If not, maybe I will ask the dentist for an extra shot of novicaine to take the edge off what seems to me a code loop-hole/over-sight.Jim B said:Papio Bldg Dept,I know that you have asked this question of Mark:
But there are exceptions under IBC 2009; 1104 for providing accessible routes to non-grade level floors.
Keep in mind that these exceptions are only for accessible routes, not other features or fixtures specified in Chapter 11 unless specified. The concept is that an accessible route (ramps, sloped surfaces) tends to benefit wheelchair users while a person may have a visual or hearing impairment or may be on crutches and may still navigate stairs.
Also in the future, there may be an addition that will drive accessible routes to these levels; if so, the features and fixtures are already accessible.
Also, as per my previous posts, if your jurisdiction has adopted the I-Codes and the reference standards that the IBC may refer to, then the stairs that you have questioned do not need to meet ANSI A117.1-2003 requirements since IBC Chapter 10 never references ANSI A117.1-2003 for stairs.