This might be a question for a forum like Mike Holt's, but I just encountered something I had never heard of before.
An engineer spec'd a 42 pole panel with 24 breakers and 18 spaces. The panel that was installed had long buss bars, but the there was a metal cover where the 18 spaces would go and no way to connect a breaker. The manufacturer claims that the size of the panel and the long buss bars gave us "space" for 18 additional breakers, but the electrician should have ordered "provisions" to be able to mount additional breakers in the space provided.
When I used to do mechanical/electrical engineering in the 1970s to 1990s "space" meant you just had to stab or bolt a breaker in.
Is this a new industry standard, or just one manufacturer's attempt to squeeze additional $ out of a project?
An engineer spec'd a 42 pole panel with 24 breakers and 18 spaces. The panel that was installed had long buss bars, but the there was a metal cover where the 18 spaces would go and no way to connect a breaker. The manufacturer claims that the size of the panel and the long buss bars gave us "space" for 18 additional breakers, but the electrician should have ordered "provisions" to be able to mount additional breakers in the space provided.