1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

The Official Electrical Violation Photo Thread

Discussion in 'Electrical Codes' started by jar546, Nov 24, 2018.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    I would like this to be an ongoing thread where we not only post photos of NEC violations but also cite the applicable codes so that everyone has an opportunity to learn or dispute the violation.

    I will start it off with this photo that is a violation of NEC 334.12(B)(4) as confirmed by 300.5(B) and 300.9

    IMAG0100.jpg
     
  2. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,316
    Likes Received:
    72
    You’re certainly working for the right company to see violations daily.
     
    jar546 likes this.
  3. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    [​IMG]

    210.52(C)(1) Wall Countertop Spaces. A receptacle outlet shall be installed at each wall countertop space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.

    And if there is no wall? What then?



    [​IMG]

    210.52(E)(5) Receptacle Outlet Location. Receptacle outlets shall be located on or above, but not more than 500 mm (20 in.) above, the countertop. Receptacle outlet assemblies listed for the application shall be permitted to be installed in countertops. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages, sinks, or rangetops as covered in 210.52(C)(1), Exception, or appliances occupying dedicated space shall not be considered as these required outlets.


    Informational Note: See 406.5(E) for requirements for installation of receptacles in countertops.


    Exception to (5): To comply with the conditions specified in (1) or (2), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base

    1. (1) Construction for the physically impaired
    2. (2) On island and peninsular countertops where the countertop is flat across its entire surface (no backsplashes, dividers, etc.) and there are no means to mount a receptacle within 500 mm (20 in.) above the countertop, such as an overhead cabinet
    This one is open to debate. The first picture is the kitchen side of the counter. The second picture is the dining room/entertainment room. So does it qualify as a violation or does it not?
     
    jar546 likes this.
  4. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    One receptacle can result in a butt load of corrections.

    [​IMG]



    210.8
    Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (D). The ground-fault circuit-interrupter shall be installed in a readily accessible location.
    210.8(A)(3)
    Outdoors.


    210.12 Arc-Fault Circuit-Interrupter Protection.
    (A)
    Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected
    210.12(B)
    Branch Circuit Extensions or Modifications ó Dwelling Units. In any of the areas specified in 210.12(A), where branch-circuit wiring is modified, replaced, or extended, the branch circuit shall be protected by one of the following:

    406.9
    (B) Wet Locations.
    (1) Receptacles of 15 and 20 Amperes in a Wet Location. Receptacles of 15 and 20 amperes, 125 and 250 volts installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. An outlet box hood installed for this purpose shall be listed and shall be identified as "extra duty." All 15- and 20-ampere, 125- and 250-volt non-locking-type receptacles shall be listed weather-resistant type.

    406.12 Tamper-Resistant Receptacles

    (A) Dwelling Units. In all areas specified in 210.52, all non-locking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
     
    #4 ICE, Nov 25, 2018
    Last edited: Nov 25, 2018
    jar546 likes this.
  5. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    It looked like a beautiful installation, until embossed in the metal of the transformer were the words "Do Not Install in Attics"

    Therefore, NEC 110.3(B) which governs the use of equipment in accordance with its labeling and instructions

    IMG_1709.jpg
     
  6. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    [​IMG]

    110.3 Examination, Identification, Installation, and Use of Equipment.
    (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.


    Note that the bottom half of the clamp has been turned in the right direction for re-bar application. It might be that the clamp is too large for a 3# re-bar.
     
    #6 ICE, Nov 25, 2018
    Last edited: Nov 25, 2018
  7. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    And fittings for the cable?
     
  8. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    You can't see them but they were the black button NM style which are listed for that use.
     
    Pcinspector1 likes this.
  9. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    Should I assume that clamp was not listed for rebar, not listed for direct burial, not listed for concrete encasement or a combination of all 3? Some are only listed for pipe and not rebar.
     
  10. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    It is just installed wrong.
     
    Pcinspector1 likes this.
  11. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    Oh that too, LOL
     
  12. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,898
    Likes Received:
    698
    ICE....AFCI for outdoor receptacles?....not a room?
     
  13. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,898
    Likes Received:
    698
    Jeff, maybe plainly state that the interior of outdoor conduits is a wet locations well....? I think it helps to know what the actual problem is as well as the code section...

     
  14. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,689
    Likes Received:
    674
    It is not a home run.....it is a circuit extension. That’s almost always the case.
     
    #14 ICE, Nov 26, 2018
    Last edited: Nov 26, 2018
  15. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,898
    Likes Received:
    698
    Ahhhh...got it....
     
  16. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    Just how many violations do you see here? I will list 1 violation, see if you can list more.
    First, this is a 3 prong receptacle fed by a 2 wire extension cord cable.
    The first violation I will list is:
    NEC 400.8 under Uses Not Permitted, NEC 400.8(1) "As a substitute for the fixed wiring of a structure"

    IMG_1949.JPG
     
  17. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,853
    Likes Received:
    283
    Cite the violation here. You can either use the IRC electrical section or the NEC for your answer.

    IMG_2026.JPG
     
  18. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,943
    Likes Received:
    249
    Depth of box below surface of gypsum - E3906.5
    Don't know intent of box - weight support requirement - minimum E 2905.6.2
    Metallic box must be grounded - E 3905.2 - See hint of green wire, cannot see details for grounding.
     
    Msradell and jar546 like this.