Stairs from audience to stage, typical high school. These stairs are definitely not required for egress. I recommended they be left out. Owner insisted for convenience. Stairs are 33" wide. Shop drawings showing 29 11/16" clear. I think these can be 36" wide by the less than 50 occupant load exception but I don't think any stairs (with a very few exceptions for restricted access where 22" clear is permitted) can be under 36" clear in an auditorium. Is my reading of the IBC correct?
Thread 'Mezzanine grows and becomes a second floor'
Given: A nonsprinkled office space with an upper level mezzanine would like to expand the mezzanine into an adjacent tenant space. But then the area of the mezzanine will exceed the allowable ratio when compared to the open and unobstructed area below. Therefore the upper level will become a second story rather than a mezzanine. The mezzanine is surrounded by a guard rail and the stairway is open / unenclosed. Question: After establishing that the upper level is no longer a mezzanine and...
2018 IBC. I am trying to figure out an allowable area. I will try to articulate it as best I can. I don't see it working as non-separated. But using separated I am not so sure. When using equation 5-1, for either separated or non-separated we use the multiplier for frontage increase. Is the same frontage increase multiplier used for both separated and non-separated calculations? In other words, using non-separated, (F) is the entire building perimeter that fronts on the public way...
I'm designing a 2 story, 3,000 sf building (parking on Level 1, dental clinic on Level 2) with an elevator, in Florida. Per FBC Chapter 9, I don't need a fire alarm. (Group B, not an ambulatory care facility). However, am I missing something and do need one?
Do outside air intakes for HVAC equipment in a Wildland Urban Interface zone require flame and ember resistant vents, or are these special vents only required at passive ventilation locations such as for an attic or crawlspace? The project is a commercial building, but the same question would apply to a residential building.
Thread 'Under 50 occupants second exit requirement'
Portland, OR I’m attempting to figure out egress for a new café/donut shop going into an existing cafe's space. The occupancy works out to 48 people with A-2 occupancy in the dining area and Business in service areas and in the kitchen. Non-sprinklered, VB construction. There is currently only one exit with signage at FOH (front of house) and we want to see if we can keep it that way. I talked with a plans examiner for the City today in an attempt to figure out how to overcome our not...
Michigan building Code 2021, I have a small after school care building that they are wanting to have a mezzanine in the space. The space is open to below and used for tv and lounge type activities. Total building square footage is only 7000 sf with the mezzanine only being 1500 sf. I am not seeing how I can consider this anything other than and Educational use group as a Daycare since its minors being supervised. Section 903.2.3 Group E states An automatic sprinkler system shall be...
In the IBC 2021 code 1014.6 on Handrails, it states that the handrail is required to return to the wall, and be continuous, among other things, but not important to this question. When I was in the field I always had inspectors tell me the continuous part meant you could not use a miter and had to use the premade cured 90 to return to the wall. Now that I'm in a different role and different area, contractors argue that part (the curve not the return to the wall) and miter the wood rail. Why...
[BG] COMPUTER ROOM. A room or portions of a building used primarily to house information technology equipment (ITE) and serving an ITE load less than or equal to10 kW or 20 W/ft2 (215 W/m2) of conditioned floor area.
Thread 'IBC 1023.7 - Interior exit stairways and exterior walls'
I got flagged in permit review for not addressing this section of 2018 IBC. I have a type VA building with 1-hour exterior bearing walls and 2-hour shafts (4 story R2 on 1 story S-2 garage). Does 1023.7 apply if my walls are already 1-HR per table 601 and 705.5? What about the openings? Could the 10' distance rule be omitted if the stair enclosure had 3/4 hr protected openings? Situation similar to below: Thanks y'all.
I have someone looking at a project that involves an addition to an existing historic building. The existing construction is generally non-combustible (concrete and masonry) and the proposed project could meet height and area requirements including the new addition with a construction type of IIA. At issue is a tall library space that has full height shelving, and a walkway at an intermediate level to access higher shelving. The walkway is of unprotected steel construction. Applicable...
I'm doing a dentist office build-out The entire space is >3000 sf which requires a vestibule. I'm trying not to do a vestibule. There is a place in the plan where if I put a door in a hallway if would divide the entire space in 1/2. See attached plan Would this be within the intent of the code?
2021 IBC in Massachusetts 1604.2 Strength Buildings and other structures, and parts thereof, shall be designed and constructed to support safely the factored loads in load combinations defined in this code without exceeding the appropriate strength limit states for the materials of construction. Alternatively, buildings and other structures, and parts thereof, shall be designed and constructed to support safely the nominal loads in load combinations defined in this code without exceeding...
Existing building, just a few years old, under the same code administered when it was originally constructed. 2 story, VB, NFPA 13, non-sep. mixed use B,M,S1,A2 (A2 most restrictive). 2 suites were left unfinished core shell spaces, main suite consistes of a small warehouse, offices, conference room. Proposal now to make one of the 2 unfinished units an apartment (they call it a "caretaker suite"). Does not work as a live-work due to the restrictions. A few questions for a meeting...
Thread 'Mechanical Duct Work "shaft" in Two Story Building'
I'm hoping to confirm my understanding that a vertical opening in a non-rated floor assembly that is only connecting two stories does not need to be a rated shaft assembly. The building is IIIB, Two stories, and sprinklered. Although per NCBC 717.6.3, I don't think it being sprinklered makes a difference. As long as we comply with #2 the walls around the mechanical shaft do not need to be rated. We comply with 712.1.9 but i don't know that this section applies because it says it pertains to...
2018 IBC w/ NC amendments Are windows permitted on an interior wall of an exit passageway? The way I read section 1024.5, the answer is no. When I read the commentary, it appears that window assemblies tested as wall assemblies are be permitted. Thanks
I need a scan or a photo of the section from BOCA 1970 (or some year as close to 1970 as possible) on Certificates of Occupancy. For 1970 it was section 120.1 -- the number might be different in other years. I have the language from my state's adopted version, but we revised that section and I need the BOCA model code language as a comparison. If anyone has access to an unedited BOCA Basic Building Code from 1970 or thereabouts, please contact me -- or just post a scan of it here. I'm...
typically a Townhouse gypsum separation wall extends to the interior side of the exterior sheathing of the perpendicular exterior wall. Of course the exterior sheathing is fire rated and extends 4' to each side . My questions are...1. can the separation wall terminate into solid blocking within the wood framed exterior wall...solid 2 x 6's..rather than the back of the exterior sheathing. 2. If there is a gap between the separation and the exterior sheathing..1" or so..can that gap be filled...
Per Ch 29 of the IBC the prescribed distance to travel in a factory setting is 500 feet or approved distance by the AHJ. Is it the intent of the code to have the path completely indoors or can an exterior path comply as in a campus type setting? Thanks!
New PEMB building, unconditioned, no utilities, used for storing grounds maintenance equipment storage. Curious about the different ways I see this classified?
So is there a reason why several of the entries (B, E, I, etc) do not have a dividing line between the male and female columns as do the A occupancies? I would think there would be a reason but the only thing that would make sense is that you do not divide the occupant load into 2 sexes which is not correct...any thoughts? Thanks!
Massachusetts State Building Code 9 or 10th edition table 307.1 (1) MAQ hazardous material limits. Need reference standard, code verse industry standard for calculating the quantity include the container full or empty. Thank you
This may be a stupid question... What do the dashes in table 508.4 means? For example if you look at B to R is a dash, but R to B is a value (1 or 2)
Multifamily Project, 1-hour Wood I-Joist Floor Assemblies with a 1-hour rating: I'm having trouble finding any ceiling radiation dampers for wood I-joist floors. It seems like they are only fire tested with wood truss floor assemblies. I'm not sure why this is. Anyone know why this might be and if there is a code acceptable path towards ceiling radiation damper in 1-hour I-joist assemblies? Or is this an AHJ question?
I recently observed a large apartment project in Florida, where the entire structural system was built out of cast-in-place reinforced concrete. What stood out was the method: large steel gang forms, resembling container boxes, were craned into position to create one apartment “box” at a time. Concrete was poured in place, allowed to cure, then the forms were stripped and moved to the next unit. The end result looks like a stack of concrete boxes, side by side and then above, until the...