Paper Towel Dispenser in WC Clear Space?

What I am talking about is that there is a shelving unit that is 36" long against the wall and comes out 30" from the wall, is 6' high, 5 shelfs, lowest shelf is 3" from the floor. I am sure many of you have this type of shelf unit in your garages or basements. It is between the toilet and the sink. They are keeping supplies for the toilet room on it.
 
Toilet has a automatic flusher. The problem is the code allows shelving in the water closet clear space but has no limit in how large or where it is. They could even put shelving between the toilet and wall. When I fail inspection I am required to state a code section and there is nothing I can use for this.
 
Have to slouch to use it? Picture would be helpful. Even if automatic it still has the push button that needs to be accessible.
 
Toilet has a automatic flusher. The problem is the code allows shelving in the water closet clear space but has no limit in how large or where it is. They could even put shelving between the toilet and wall. When I fail inspection I am required to state a code section and there is nothing I can use for this.
ICC A117.1
604.3.3 Clearance Overlap. The required clearance around the water closet shall be permitted to overlap the water closet, associated grab bars, paper dispensers, sanitary napkin receptacles, coat hooks, shelves, accessible routes, clear floor space at other fixtures and the turning space.
No other fixtures or obstructions shall be within the required water closet clearance
 
ICC A117.1
604.3.3 Clearance Overlap. The required clearance around the water closet shall be permitted to overlap the water closet, associated grab bars, paper dispensers, sanitary napkin receptacles, coat hooks, shelves, accessible routes, clear floor space at other fixtures and the turning space.
No other fixtures or obstructions shall be within the required water closet clearance

That is what I am saying. There is no limit on how much the shelves take up of if they need to be mounted to the wall.
 
Would 609.3 (projecting objects above & below grab bars) help? The rear grab bar is supposed to extend beyond the edge of the toilet (604.5.2).
 