Mr. Inspector
An office has a electric instant hot water heater in a closet that has a 30" door. Would this closet be considered a room and need to have a 36" door? Or does the room the closet is in only needs to have a 36" door? Or both? Or does any of these doors opening need to be not less than 36"?
306.2 Appliances in rooms. Rooms containing appliances
shall be provided with a door and an unobstructed passage-
way measuring not less than 36 inches (914 mm) wide and 80
inches (2032 mm) high.
Exception: Within a dwelling unit, appliances installed in
a compartment, alcove, basement or similar space shall be
accessed by an opening or door and an unobstructed passageway
measuring not less than 24 inches (610 mm) wide
and large enough to allow removal of the largest appliance
in the space, provided that a level service space of not less
than 30 inches (762 mm) deep and the height of the appliance,
but not less than 30 inches (762 mm), is present at
the front or service side of the appliance with the door
open.
open.