They need to be installed to meet whichever is the strictest between code and manufacturer instructions.smoke and CO alarms should be installed in accordance it manufacture instructions not state law
I disagree, the manufacture has had the device test by a recognized laboratory under a defined testing procedure and listed for their use, the manufactures listing always wins.They need to be installed to meet whichever is the strictest between code and manufacturer instructions.
No it does not and I challenge you to point to a code section that is specific to smoke detectors. You will find the manufactures installation requirement for other types of detectors but not smoke detectors for residential occupancies.the manufactures listing always wins.
[A] 102.1 General. Where there is a conflict between a generalI disagree, the manufacture has had the device test by a recognized laboratory under a defined testing procedure and listed for their use, the manufactures listing always wins.
I never understood how you could have a viable combination device. CO is slightly more dense than air and therefore will not rise of its own accord. Lacking air currents to carry the CO to the ceiling you'd be dead before the alarm went off. That having been said, ...No it does not and I challenge you to point to a code section that is specific to smoke detectors. You will find the manufactures installation requirement for other types of detectors but not smoke detectors for residential occupancies.
According to all that I can find on the internet, CO is not heavier than air and will disperse evenly in air. The alarm manufactures allow the alarms on walls as well as ceilings with restrictions from things that move air such as fans and HVAC registers,I never understood how you could have a viable combination device. CO is slightly more dense than air and therefore will not rise of its own accord. Lacking air currents to carry the CO to the ceiling you'd be dead before the alarm went off. That having been said, ...
[RB] MANUFACTURER’S INSTALLATION INSTRUCTIONS. Printed instructions included with equipment as
part of the conditions of their listing and labeling.
If you violate the manufacturers' installation instructions you void the listing.
let me work on thatNo it does not and I challenge you to point to a code section that is specific to smoke detectors. You will find the manufactures installation requirement for other types of detectors but not smoke detectors for residential occupancies.
I do not have an answer to your question. The following code might shed some light on the issue of lights in that the lights are just a part of the 3 VA.ICE
Just curious
The general lighting load is based on 3 VA per sq ft. Is that using incandescent light bulbs or LED? Wouldn't LED's reduce that number quit a bit if the 3va per sq ft factor is based on incandescent light bulbs.