• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

An average day

The cluster of cable in the single clamp is a code violation.
With that panel design and a large number of cables entering it, there is no other way except a large Romex® connector to bring them in, they could have at least snugged it up instead of leaving it loose. That is one of the weak points of the meter main panels like that, rather then the East Coast style of the meter can outside & the panel inside.
 
Derating yes, securing, maybe...NM needs to be supported within 12" of the box, not necessarily at the box...Right? 334.30...I know there is something else there, but Shirley one of the sparkys will correct me....
 
I do not believe they need to be derated because they are not bundled for more than 24". However, the clamp is not listed for that many conductors, and is thusly a violation. I have written it up, but the only possible hazard I see is the cables rubbing on the exposed screw threads.
 
I do not believe they need to be derated because they are not bundled for more than 24". However, the clamp is not listed for that many conductors, and is thusly a violation. I have written it up, but the only possible hazard I see is the cables rubbing on the exposed screw threads.
Still goes back to the design of that panel leaving no other option but stuff a bunch of cables into a larger Romex® connector.
 
312.5(C) Cables.
Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.


This is from the handbook:

20220906_132851.jpg

This is something that every electrician should learn early in their career. If they learn it from me it’s a bitter pill to swallow. I am okay with that. The rub is that it can be such a bitch to fix. The workman wants to hear from me why fifteen cables in a clamp is a safety issue worth the grief. I hear, “Can you let it goe this time?” If I let it go this time why would the correction have any merit next time….and there will be a next time.
 
Last edited:
Is it a cabinet? Or just a panelboard? We don't get a whole lot of cabinets in houses here...Unless they are not metal... ;)
The paneboard is in a cabinet…cutout box..

UL has the following definition (UL White Book CYIV):
This category covers sheet-metal boxes and nonmetallic boxes. Cutout boxes are provided with a door secured by hinges and one or more fasteners and are intended for surface mounting. A cabinet consists of two parts:
a cabinet box and a mating cabinet front that contains a door. A cabinet may be flush mounted or surface mounted. These boxes are intended for installation in accordance with Article 312 of ANSI/NFPA 70, ‘‘National Electrical Code.’’
 
Last edited:
Commentary from the handbook is not enforceable, & there still is no way to do what you are saying with a large number of cables, there is physically not enough room to have individual Romex® connectors. Might be time to ban that style of panel.
 
Commentary from the handbook is not enforceable, & there still is no way to do what you are saying with a large number of cables, there is physically not enough room to have individual Romex® connectors. Might be time to ban that style of panel.
The handbook is someone's opinion of what is enforceable. There's two ends to the cabinet and both ends provide KOs. On top, or bottom, of that is the use of a Greenlee punch.

If that cabinet won't work....oh well....try another.
 
# ~ # ~ #

The whole idea of convenience to the contractors is

more valued than Code compliance, seems to be the
politically & culturally correct norms.........Enforcement
of the legally adopted Codes & Standards, for some,

...seems to be in theory only.

Hammurabi had the same issues in his day too !


# ~ # ~ #
 
312.5(C) Cables.
Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.


This is from the handbook:

View attachment 9448

This is something that every electrician should learn early in their career. If they learn it from me it’s a bitter pill to swallow. I am okay with that. The rub is that it can be such a bitch to fix. The workman wants to hear from me why fifteen cables in a clamp is a safety issue worth the grief. I hear, “Can you let it goe this time?” If I let it go this time why would the correction have any merit next time….and there will be a next time.
I don't do electrical, but I've seen hundreds of panels here and have never seen more than one wire per knockout (that I've noticed I guess). Moreover, I have not seen cables bundled at all. wires are individually run down the wall, stapled, and run at a right angle into to panel one by one.
 
I don't do electrical, but I've seen hundreds of panels here and have never seen more than one wire per knockout (that I've noticed I guess). Moreover, I have not seen cables bundled at all. wires are individually run down the wall, stapled, and run at a right angle into to panel one by one.
Must be a local thing. I see multiple wires per KO clamp typically all coming out the top. The very common 3/8" cable clamps allow up to (3) 14/2 in one clamp.
 
The inspection was for a final of a water main to an apartment building. The pipe size has increased so the original ground clamp is too small. For that reason, the plumber ignored the clamp. I had to tell him to replace the clamp.

IMG_4041.JPG


The plumber installed almost the correct clamp. It is not too much worse than the original clamp so it is acceptable...well that and the armor is short. I then had to tell the plumber to seal the wall.

20220912_144320.jpg


He took care of it. The clamp picture and the caulk picture were sent to my phone so no return trips were necessary.


20220913_154448.jpg
 
Last edited:
The job is a furnace and AC.

The contractor and the owner were both upset because they had to wait for me to arrive. The story is that today was the fourth inspection. The AC has no equipment ground with the feeder. The equipment ground from the condenser to the disconnect is a red wire with white tape.

The dwelling is so large that it has to be called a dwelling and not a house. There is a furnace and I know that because there is a correction regarding a sediment trap and the apparently the B-vent has a downward slope. The contractor's representative didn't know where the attic access is located so no ladder was set up....or perhaps he thought I was just going to sign off on the job since this was the fourth inspection.

Thje owner showed us a two by two foot plywood hatch in the garage wall and said that the furnace is behind that. He had to move a car that was in the way of where the ladder had to be but after five minutes of failing to start the car he summoned his wife and she started the car. He said that the car knows the difference between him and her. Well then the workman removed a bunch of screws and the plywood. He said that he sees nothing but duct for about thirty feet and then there is a turn. So the furnace must be around the bend. I didn't go looking for it.

I told the workman that his company has no room to complain but the owner had removed himself and got the message from the correction slip. I anticipate a complaint.

Oh and to get to the AC disconnect it was a tight squeeze between two condensers, a tree and some bushes. My back got scratched and my shirt was torn. Had I been the first inspector that would have been the first correction.



IMG_4056.JPG
 
Last edited:
The inspection was for a swimming pool final. The car gate is the barrier to the pool. The car gate was approved at the pre-plaster inspection. The contractor stated that a condition of approval is that the gate be electric and close automaticaly with a thirty second delay. There will be thirty seconds to get the car past the gate because it will close ...blocked or not. I found plenty of other corrections so I didn't have to turn it down just because of the gate.

IMG_4062.JPG



The panel is held up by an 1.5" pvc pipe. It will move with the wind. Well until the two sheet metal screws pull out.

IMG_4059.JPG


The junction box has already bent to the wind.


IMG_4058.JPG
 
Last edited:
This thread became soooo off topic that I placed a reply here where it wouldn't matter.

The topic became what a lousy inspector does when he's bored. If you don't believe me take a look at the thread.

Here is an example of a no code violation, violation.

The inspection was for a reroof final. The two halves of the building come together in a less than attractive manner. The valley is skewed to the left. It should start at the top in the picture and the bottom should line up near the rear tire on the truck. The structure is not balanced ... the feng shui is whacked.

IMG_4089.JPG

You can see that the valley was cut from the right side.....the side that leans into the flow. Can I get a code for that wrong way this was done? Help me out with that.

The correction said, "Create a valley that sheds water instead of bucking water." Sheds and bucking are not found in the code as they relate to a roof valley.

Had the cut been made coming from the left the only wrong would be the ugly. So there you have it. I didn't invent a code but I did write a correction with no code (so far).

The inspection was yesterday at a city where I was a temp so I’ll not find out if the contractor complied.

IMG_4088.JPG


IMG_4087.JPG
 
Last edited:
The job is a bathroom remodel. The plan is to install a receptacle in the back of a drawer. The cord is robust. The contractor claims to have done it many times.

20220913_083447.jpg

20220913_083453.jpg
 
We have done that many times in commercial (retail) millwork. It sounds great on paper, in practice it's not as successful for a convenience outlet. Works ok for a charging station.
 