An average day

There is a weep screed and it should be 2" above the concrete. The lath is self furring but they managed to overcome that feature with staples at 6" on center.
 
This is a correction written during a water heater inspection. Does a water heater have a tail piece?
IMG_0141 2.jpeg
 
Last edited:
This correction was written during an inspection of a room addition. There is no mechanical or electrical plan and the inspector has told them to submit plan revisions to the plan check engineer. Asking for installation instructions for mounting mini-splits?

IMG_4170.jpeg
 
Last edited:
Doesn't it have to be seismic in Cali?...They say you are tough.....I wouldn't be too critical of the word tailpiece, plans for residential? or commercial job?
 
Doesn't it have to be seismic in Cali?...They say you are tough.....I wouldn't be too critical of the word tailpiece, plans for residential? or commercial job?
When an inspector doesn't know the terminology it is no surprise that the correction states that the T&P + the smitty pan
shall have a drain that terminates no more than 6" above grade.

The compressor is a skinny little mini-split at a residence. There was no mechanical plan to revise, and who the Heck would ask
for a plan check review of the anchorage to a plastic platform sitting in the yard.
 
Last edited by a moderator:
IPC T&P termination

10. Terminate not more than 6 inches (152 mm) above
and not less than two times the discharge pipe diameter
above the floor or flood level rim of the waste
receptor.

Pan drain

504.7.2 Pan drain termination. The pan drain shall
extend full size and terminate over a suitably located indirect
waste receptor or floor drain or extend to the exterior
of the building and terminate not less than 6 inches (152
mm) and not more than 24 inches
 
608.5 Discharge Piping. The discharge piping serving a temperature relief valve, pressure relief valve, or combination of both shall have no valves, obstructions, or means of isolation and be provided with the following:

(3) Discharge pipe shall discharge independently by gravity through an air gap into the drainage system or outside of the building with the end of the pipe not exceeding 2 feet (610 mm) and not less than 6 inches (152 mm) above the ground and pointing downwards.
 
ICE, Post 4,248, any back story on this? Need more information before I scrutinize the caption.:eek:
 
So.. what column and method from table 300.5 would address this application?

Ridged nonmetallic raceway below a sidewalk?

Service to ADU size?
 
So.. what column and method from table 300.5 would address this application?

Ridged nonmetallic raceway below a sidewalk?

Service to ADU size?
Column 3 ....under minimum 4" thick concrete slab....so it is deep enough.....however it is NMC that is not allowed in a wet location......the conduit is schedule 40 and shall be schedule 80 where it is above ground...the conduit is too small in diameter for the eventual conductors.....the pull box is too small and shall be inset into the wall.
 