So could they run individual THHN conductors?
THHN No. A conductor that is listed for a wet location is required.
Last edited:
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
So could they run individual THHN conductors?
Learn sumtin eberyday aroun hear. But you made me look it up, you old goat. The wire needs “w” in the name to be in a wet location. THWN would work.THHN No. A conductor that is listed for a wet location is required.
We usually see the poly over the aggregate here, is this an engineers design?
No.East LA project?
The job is an electric service upgrade. The son-in-law of the 91 year old owner called to tell me that he was having trouble with the contractor. There was an inspection set for that day and he was concerned because the electric dryer wasn't working. The contractor didn't show up.
Well there's your problem.
Yet another service mounted over the old location with the conductors leaving through the back of the cabinet. It's a good thing that I'm a combination inspector 'cause I can write more than electrical code violations.
At the first inspection I found two appliance connectors. We allow one and it is to be used as an appliance connector. I wrote a correction to replace the second flex connector with hard pipe. The contractor installed CSST instead of hard pipe. Now he gets to intall a solid #6 bonding jumper from the hard pipe to the grounding electrode system.
View attachment 5981
Black CSST may not need the bonding wire, check manufactures install instructions.