Yankee
Your red highlighted line only is applicable when there is NO LIVING SPACE ABOVE. Please see chart. Ist block SEPARATION FROM THE RESIDENCE means the living space adjacent AND any living space ABOVE, being supported by the ceiling/floor assembly.mtlogcabin said:R302.6 Dwelling/garage fire separation.The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
My understanding is the wall in question is perpendicular to the dwelling unit (exterior wall) Section 302.5 does not apply
The wall will have two 2x top plates fill the annular space where the electrical wire penetrates the top plate with fire caulk and don't worry about it.
R302.6 Dwelling/garage fire separation. The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
TABLE R302.6 DWELLING/GARAGE SEPARATION
SEPARATION | MATERIAL |
From the residence and attic | Not less than 1⁄2-inch gypsum board or equivalent applied to the garage side |
From all habitable rooms above the garage | Not less than 5⁄8-inch Type X gypsum board or equivalent |
Structure(s) supporting floor/ceiling assemblies used for separation required by this section | Not less than 1⁄2-inch gypsum board or equivalent |
Garages located less than 3 feet from a dwelling unit on the same lot | Not less than 1⁄2-inch gypsum board or equivalent applied to the interior side of exterior walls that are within this area |