gfretwell said:
How did you connect the generator to the well pump in a code compliant way? Was that well pump listed for cord and plug connection?
590.1 Scope.
The provisions of this article apply to temporary
ELECTRIC POWER and lighting installations.
590.4(E) Disconnecting Means. Suitable disconnecting switches
OR PLUG CONNECTORS shall be installed to permit the disconnection of all ungrounded conductors of each temporary circuit. Multiwire branch circuits shall be provided with a means to disconnect simultaneously all ungrounded conductors at the power outlet or panelboard where the branch circuit originated. Identified handle ties shall be permitted.
(H) Protection from Accidental Damage.
Flexible cords and cables shall be protected from accidental damage. Sharp corners and projections shall be avoided. Where passing through doorways or other pinch points, protection shall be provided to avoid damage.
Commentary- Flexible cords and cables, because of the nature of their use, are permitted to pass through doorways, unlike the requirement in 400.8(3).
Well pumps have no listing as to the means of disconnect. Where does that idea come from?
I usually open the disconnect at the well and terminate the cord that plugs into the generator to the load conductors per the following section of the NEC
(I) Termination(s) at Devices.
FLEXIBLE CORDS and cables entering enclosures containing devices requiring termination shall be secured to the box with fittings designed for the purpose
gfretwell said:
BTW "cold" is a relative thing. Cold in North Carolina is not Minnesota cold.
Cold defined- Feeling no warmth; uncomfortably chilled. Is this not about the same time that we get up to doing something about being cold. Do not people in the Sunshine state have some sort of heat? What is your coldest temp? The house I lived in on Pa. Ave. in Altamonte Springs had an electric heater in the hall wall and the two years I lived there I didn’t see any ice anywhere although the second winter I did turn on the heat a couple of times. There are ways to use one of the small generators correctly. You can even connect them to your home’s wiring system as long as it is done by the code. The code says only as a SDS. Knowing this why do we keep trying to make one excuse after another to do it incorrectly?