ICE
Oh Well
The inspection request was for framing and rough electrical of an ADU The person that met me is a young man that says that he is studying to become a contractor. The plans call for shear walls wherever there is no opening. There are no shear walls and few anchor bolts. The only window into the bedroom is 14" wide. Drywall screws were used on the plywood. There is an electrical panel in a clothes closet. There is a new roof and no attic ventilation. No smoke or CO alarms wired. It was 108° and I wrote 18 corrections before I noticed the drywall screws.
The young man was polite and not even a hint of upset. I felt sorry for him. The guy in the next post is a jerk.